Bacnet Server
I guess you restarted the controller as you mentioned ‘read during startup’
I don’t think that enabling that parameter had anything to do with your issue...
Restarting is causing the priority array to be cleared and i think your issue is that you wrote a value in the array at a higher level then the default 16.
If you write any value at a higer prio in the array then this value is overruling the values comming from the GA.
What is the default prio in your 3th party software? I see some manufacturers using 10 as default.
Try to change a value from the client side, and check if it sets the value in the prio array at a higher level then 16.
Bacnet Server - by Tokatubs - 04.04.2019, 21:16
RE: Bacnet Server - by Erwin van der Zwart - 05.04.2019, 05:32
RE: Bacnet Server - by Tokatubs - 05.04.2019, 08:49
RE: Bacnet Server - by admin - 05.04.2019, 09:19
RE: Bacnet Server - by Tokatubs - 05.04.2019, 09:45
RE: Bacnet Server - by eirik - 05.04.2019, 18:46
RE: Bacnet Server - by Tokatubs - 06.04.2019, 20:56
RE: Bacnet Server - by Tokatubs - 09.04.2019, 08:08
RE: Bacnet Server - by Daniel - 09.04.2019, 08:21
RE: Bacnet Server - by Tokatubs - 09.04.2019, 10:21
RE: Bacnet Server - by admin - 09.04.2019, 08:29
RE: Bacnet Server - by Tokatubs - 09.04.2019, 09:01
RE: Bacnet Server - by admin - 09.04.2019, 09:37
RE: Bacnet Server - by admin - 09.04.2019, 10:33
RE: Bacnet Server - by Tokatubs - 10.04.2019, 09:43