05.04.2019, 08:49
	(05.04.2019, 05:32)Erwin van der Zwart Wrote: Hi,
I guess you restarted the controller as you mentioned ‘read during startup’
I don’t think that enabling that parameter had anything to do with your issue...
Restarting is causing the priority array to be cleared and i think your issue is that you wrote a value in the array at a higher level then the default 16.
If you write any value at a higer prio in the array then this value is overruling the values comming from the GA.
What is the default prio in your 3th party software? I see some manufacturers using 10 as default.
Try to change a value from the client side, and check if it sets the value in the prio array at a higher level then 16.
Thanks for answer, Erwin.
I am only using AI block to show temperature. So i only link the Ai block to the bacnet adress of the Lm. I guess this block dont have priority.
On the logic machine i only click the export frame. And use yabe to get the adress.
Did not do any restarting. I just clicked the "read on startup" just in case. And set polling time on the GA in the Objects list.
You see from attached pic that the block goes into "Target object unknown" before it goes back to normal.
On the bottom it has the value, then goes into alarm because the object returns unknown.
Have been doing integrations from knx/bacnet using this program before but have not tried using the Lm before. So have not seen this behaviour.
Tried using the bacnet client, with no success. Guess this only supports BAC0. On this site we use Bac2.