This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Gateway Modbus RTU to Modbus TCP
#4
Actual Modbus addressing starts from 0. Documentation for some devices have addressing starting from 1 which creates confusion.

Here's modified slave script where you can specify addresses directly and there can be gaps in register map, for example: 0..15 for meter 1; 100..115 for meter 2 etc.

This script supports 16-bit values only. If only one way communication is needed (Modbus values are read-only) then it can be modified to support 32-bit and 64-bit values internally without additional scripts for splitting values into 16-bit parts.

Code:
if not mb then
  require('luamodbus')

  -- list of coil mapping, register mapping and register data types
  coils, registers, regdt = {}, {}, {}

  -- coil definition
  coils[ 0 ] = '1/1/1'
  coils[ 1 ] = '1/1/2'

  -- register definition
  registers[ 0 ] = '2/2/2'
  regdt[ 0 ] = dt.int8
  
  registers[ 1 ] = '2/2/3'
  regdt[ 1 ] = dt.uint16

  -- knx group write callback
  function knxgroupwrite(event)
    local value

    -- try to find matching coil
    for id, addr in pairs(coils) do
      if event.dst == addr then
        value = busdatatype.decode(event.datahex, dt.bool)
        mb:setcoils(id, value)
      end
    end

    -- try to find matching register
    for id, addr in pairs(registers) do
      if event.dst == addr then
        value = busdatatype.decode(event.datahex, regdt[ id ])
        mb:setregisters(id, value)
      end
    end
  end

  -- coil write callback
  function mbwritecoils(coil, value)
    local addr = coils[ coil ]
    if addr then
      grp.write(addr, value, dt.bool)
    end
  end

  -- register write callback
  function mbwriteregisters(register, value)
    local addr = registers[ register ]
    if addr then
      grp.write(addr, value, regdt[ register])
    end
  end

  -- knx group monitor, handles group writes
  busclient = require('localbus').new(0.1)
  busclient:sethandler('groupwrite', knxgroupwrite)

  -- modbus slave, listen on all interfaces and default port 502
  mb = luamodbus.tcp()
  mb:open('0.0.0.0', 502)

  -- setting slave id is optional
  -- mb:setslave(1)

  mb:setreceivetimeout(0.1)
  mb:setmapping(table.maxn(coils) + 1, 0, table.maxn(registers) + 1, 0)

  -- init coils
  for id, addr in pairs(coils) do
    value = grp.getvalue(addr)
    mb:setcoils(id, value)
  end

  -- init registers
  for id, addr in pairs(registers) do
    value = grp.getvalue(addr)
    mb:setregisters(id, value)
  end

  -- set callbacks for coil and register write
  mb:setwritecoilcb(mbwritecoils)
  mb:setwriteregistercb(mbwriteregisters)
end

-- handle modbus and knx
mb:handleslave()
busclient:step()
Reply