01.11.2019, 12:24
(28.10.2019, 08:25)Daniel. Wrote: HiHello,
Start from using RTU Read test. Select holding registers, slave id and address. You may need to subtract -1 from register address so try both ways. If this works then let me know and will make example of profile.
BR
Sorry for replying so late, the pumps are in a remote location and I have lost contact with them.
I have attached a screenshot with the correct reading settings for pump pressure (register 301 in documentation). You were right, I needed to subtract 1.