05.11.2019, 07:35
Hi,
You probably have buttons with active state objects, when the feedback is out of sync you can have this issue, the objects are probably missing telegrams due to (momentarily) high TP load, you need to check the load and most important the TP repeats, Ack all grp telegrams might solve the issue.
Also make sure to set read during startup on the feedback objects and make sure the read flags are enabled in the ETS when you set this checkbox. This keeps the objects in sync when the controller has been disconnected from the TP.
BR,
Erwin
You probably have buttons with active state objects, when the feedback is out of sync you can have this issue, the objects are probably missing telegrams due to (momentarily) high TP load, you need to check the load and most important the TP repeats, Ack all grp telegrams might solve the issue.
Also make sure to set read during startup on the feedback objects and make sure the read flags are enabled in the ETS when you set this checkbox. This keeps the objects in sync when the controller has been disconnected from the TP.
BR,
Erwin