Hi,
Hard to say exactly as it depends on other processes in your controller like amount of KNX object updates etcetera. The indicator of limitations is most of the time the CPU load.
We tested a lot of scenarios / addressable limits and you can see them in this document: https://www.schneider-electric.com/en/download/document/AN017/
On page 13 you can see the results of a test with 1000 objects on a HW2 device (you can increase this on HW3).
So if your controller is not doing anything else then 300 objects should work just fine.
BR,
Erwin