This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

HomeLynk as Modbus TCP/IP slave
#7
Hi,

Hard to say exactly as it depends on other processes in your controller like amount of KNX object updates etcetera. The indicator of limitations is most of the time the CPU load.

We tested a lot of scenarios / addressable limits and you can see them in this document: https://www.schneider-electric.com/en/download/document/AN017/

On page 13 you can see the results of a test with 1000 objects on a HW2 device (you can increase this on HW3).

So if your controller is not doing anything else then 300 objects should work just fine.

BR,

Erwin