14.11.2019, 06:09
(This post was last modified: 14.11.2019, 06:24 by XSPA2474KW.)
Hello Daniel,
I am sending you 2 videos because the problem is still here.
As you can I see in the video I had normal measurements for the energy meter A9MEM3155 up to 11/11. On that day I backup the program from the old HomeLynk and I restore to a brand new HomeLynk. From then I have not measurements.
As you can see I have make the steps according to your instructions. Old script disactivated, delete Modbus device and profile, add new profile and device, link to object and then the same error. The new profile is not show in video but I have already changed it.
Also you can see in the next video the connections from A9MEM3155 to HomeLynk. D+ to D+, D- to D- and 0V to 0V. I haven't changed anything. This connection was also in the old HomeLynk.
Please help. It is possible to be the HomeLynk broken? It is brand new.
I am sorry but I can't attached the videos. How can I send you?
Thanks
The peak on 13/11 is because I have set manually the value.
I am sending you 2 videos because the problem is still here.
As you can I see in the video I had normal measurements for the energy meter A9MEM3155 up to 11/11. On that day I backup the program from the old HomeLynk and I restore to a brand new HomeLynk. From then I have not measurements.
As you can see I have make the steps according to your instructions. Old script disactivated, delete Modbus device and profile, add new profile and device, link to object and then the same error. The new profile is not show in video but I have already changed it.
Also you can see in the next video the connections from A9MEM3155 to HomeLynk. D+ to D+, D- to D- and 0V to 0V. I haven't changed anything. This connection was also in the old HomeLynk.
Please help. It is possible to be the HomeLynk broken? It is brand new.
I am sorry but I can't attached the videos. How can I send you?
Thanks
The peak on 13/11 is because I have set manually the value.