This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus limits
#3
Thank you so much Erwin!
Everything is working properly now.
I hadn't noticed this limitation between Wiser and Spacelynk
During the weekend I temporarily implemented the script on two different plants with 32 meters the first and 28 the second.
No problem, CPU load does not exceed 0.09.
The script that reads the energy values runs every 5 minutes.
The power is read every 5 seconds.

BR,
Alberto
Reply