This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus error
#4
Physical connection might not be correct. Check A/B: sometimes they are marked incorrectly and have to be swapped. Check if GND is connected between LM and ModBus device because it might not work without it in some cases. Another thing to check is correct baud rate, parity/stop bits and slave address.
Reply