This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus error
#7
Did you try that? This is from the slave manuals.
TROUBLESHOOTING If response from RMC doesn’t happen:
- check connection from RMC and RS232/RS485 converter ;
- check if data outgoing from the RS232 serial port of the PC come in the RS232/485 converter - try to increase the wait time for response ( 300 mS is good);
- check if the transmitted data stream is EXACTLY as in example, monitoring the data on the RS485 serial line with a terminal (i.e. Hyperterminal or other emulator);
- if the RS232/485 converter is not our model EMI-1, be sure the turnaround-time is set in range 1 to 2 mS
------------------------------
Ctrl+F5
Reply


Messages In This Thread
Modbus error - by programacion2 - 10.03.2020, 07:51
RE: Modbus error - by Daniel - 10.03.2020, 08:38
RE: Modbus error - by programacion2 - 10.03.2020, 09:39
RE: Modbus error - by admin - 10.03.2020, 09:58
RE: Modbus error - by Daniel - 10.03.2020, 09:59
RE: Modbus error - by programacion2 - 11.03.2020, 07:57
RE: Modbus error - by hfebraud - 19.05.2020, 12:26