This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Anybus modbus/tcp ->mbus
#5
It is good practice to first start with 1,2 registers to check if it works. Later you can add rest of registers. Where from did you get the "readable":"true" ?? delete it, Ignore the "Read_swap" for now. You also have few registers with the same address. I would start from just meter value register 20 (datatype int64)
------------------------------