19.03.2020, 13:27
It is good practice to first start with 1,2 registers to check if it works. Later you can add rest of registers. Where from did you get the "readable":"true" ?? delete it, Ignore the "Read_swap" for now. You also have few registers with the same address. I would start from just meter value register 20 (datatype int64)
------------------------------