This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM as Modbus Slave. datatype and offset
#6
(27.11.2020, 10:11)admin Wrote: Which address are you using from ModBus side? You can only use 0 and 1 because you have 2 registers defined.
yes. use 0 and 1 registers

immediately after connecting to LM

and I can write data from Modbus Poll. But from one type PCL i can not. and from other type PLC I can only when I write float

(27.11.2020, 10:09)Daniel. Wrote: You have done everything correct here. I assume the objects 3/1/1 and 3/1/2 are 2 byte unsigned integer?
yes

I think maybe my controller starts reading not from 0, but from 16 bits. therefore, he understands part of the float as integer. And i need to do offset. is it possible?