This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP HVAC Gateway
#19
(02.12.2020, 08:29)admin Wrote: Do you mean ETS monitoring? If group address is not defined there then ETS will treat any kind of 2-byte data a floating point by default.

Yes in ETS monitoring i see difference.

Both sides are set up as 05. 1 Byte unsigned integer but in ETS monitoring KNX>LM>ModbusTCP is send as $03 Modbus responds to this. If changed on the LG controller it sends from ModbusTCP>LM>KNX it is send as 00 03 on KNX bus. In LM is see the same as value 3 including the custom value for visualisation. The 00 03 send to KNX is not recognized by the remote controller as it expects $03
Reply


Messages In This Thread
Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 08:45
RE: Modbus TCP HVAC Gateway - by Daniel - 02.11.2020, 08:47
RE: Modbus TCP HVAC Gateway - by admin - 02.11.2020, 08:51
RE: Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 09:34
RE: Modbus TCP HVAC Gateway - by admin - 02.11.2020, 09:40
RE: Modbus TCP HVAC Gateway - by KoBra - 02.11.2020, 10:32
RE: Modbus TCP HVAC Gateway - by KoBra - 18.11.2020, 16:32
RE: Modbus TCP HVAC Gateway - by Daniel - 18.11.2020, 17:03
RE: Modbus TCP HVAC Gateway - by admin - 19.11.2020, 07:51
RE: Modbus TCP HVAC Gateway - by KoBra - 20.11.2020, 14:37
RE: Modbus TCP HVAC Gateway - by Daniel - 20.11.2020, 14:40
RE: Modbus TCP HVAC Gateway - by admin - 20.11.2020, 14:41
RE: Modbus TCP HVAC Gateway - by KoBra - 23.11.2020, 09:00
RE: Modbus TCP HVAC Gateway - by KoBra - 23.11.2020, 14:58
RE: Modbus TCP HVAC Gateway - by Bortolo - 25.11.2020, 05:45
RE: Modbus TCP HVAC Gateway - by admin - 25.11.2020, 07:28
RE: Modbus TCP HVAC Gateway - by KoBra - 01.12.2020, 19:07
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 08:29
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 09:36
RE: Modbus TCP HVAC Gateway - by Daniel - 02.12.2020, 09:40
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 09:42
RE: Modbus TCP HVAC Gateway - by Daniel - 02.12.2020, 09:45
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 09:45
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 10:02
RE: Modbus TCP HVAC Gateway - by admin - 02.12.2020, 10:10
RE: Modbus TCP HVAC Gateway - by KoBra - 02.12.2020, 13:08

Forum Jump: