(11.12.2020, 12:59)admin Wrote: Thanks for the access. I've modified the persistent behavior to share the TCP connection between different devices with the same TCP connection settings (IP/port).
To minimize the CPU load you need to set "Value send delta" parameter in each mapping entry accordingly. If delta is not set then each read once per 5 seconds will update all mapped objects. Since you have a lot of mapped objects the CPU load becomes very high.
Is the only problem? I tried persistent connection in past with no success
...And i can`t change Smartlink profiles, becouse after that config button is hiding.
Thank You for fast help
(11.12.2020, 12:59)admin Wrote: Thanks for the access. I've modified the persistent behavior to share the TCP connection between different devices with the same TCP connection settings (IP/port).
To minimize the CPU load you need to set "Value send delta" parameter in each mapping entry accordingly. If delta is not set then each read once per 5 seconds will update all mapped objects. Since you have a lot of mapped objects the CPU load becomes very high.
Web UI lost connection after a while and stop refresh status. Refresh page is help for a few minutes