This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Wiser for KNX and modbus problem
#13
Alright, here is the situation:

On the line with W4K as master -> PM-3250 n°1 -> PM-3250 n°2 -> BT-Modbus -> Datamanager 2.0 we undo the branch, the situation is almost stable right now but PM-3250 keep doing CRC errors and response not from requested slave, that's strange.

Every device is on 9600 baud 8N1 and we checked for double addresses.

I even thought that maybe one of them could have 2 stop bits and not one but it's not a setting parameter, you can set it only as 8N1 and not as 8N2 plus I tried to set W4K to 8N2, 
and, that's really strange, they seems to stop making errors...

Any ideas?

Thank you very much for the help
Reply


Messages In This Thread
RE: Wiser for KNX and modbus problem - by Kilogica - 10.02.2021, 14:57

Forum Jump: