Alright, here is the situation:
On the line with W4K as master -> PM-3250 n°1 -> PM-3250 n°2 -> BT-Modbus -> Datamanager 2.0 we undo the branch, the situation is almost stable right now but PM-3250 keep doing CRC errors and response not from requested slave, that's strange.
Every device is on 9600 baud 8N1 and we checked for double addresses.
I even thought that maybe one of them could have 2 stop bits and not one but it's not a setting parameter, you can set it only as 8N1 and not as 8N2 plus I tried to set W4K to 8N2,
and, that's really strange, they seems to stop making errors...
Any ideas?
Thank you very much for the help