This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Siemens Logo modbus
#4
(21.03.2021, 09:30)admin Wrote: Have you tried using "read test" feature and reading 529 and 530, not 40529 and 40530?

I connect to the Logo through tcp, but modified the profile I was using and this worked. Thank you very much :-)
Reply


Messages In This Thread
Siemens Logo modbus - by thomasoppida - 20.03.2021, 19:10
RE: Siemens Logo modbus - by khalil - 20.03.2021, 20:24
RE: Siemens Logo modbus - by admin - 21.03.2021, 09:30
RE: Siemens Logo modbus - by thomasoppida - 21.03.2021, 09:49