You must use TPUART mode so that's correct.
Have you set the correct physical address to the device?
Default address of the device is 15.15.255 but you need to change it to the actual zone / line
where the device is connected on your KNX installation.
Use (optional) a dummy in your ETS project to declare this address so it won't be used by another device.
This could be your issue..