This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Logic Machine and PT Temperature sensor
#6
(07.04.2021, 08:15)admin Wrote: What you're describing sounds like an NTC (negative temperature coefficient) sensor. PT1000 sensors have 1Kohm at 0 degrees and the resistance get higher when the temperature gets higher.

Yes I asked and I ahve been told that this is a 10 Kohm sensor that when is heated the resistance is getting lower, so yes its an NTC sensor and I don't know if I can use it with MDTs input device then, or I must take an PT1000 along with the MDT input device
Reply


Messages In This Thread
RE: Logic Machine and PT Temperature sensor - by vmic - 07.04.2021, 08:40