(22.04.2021, 13:19)agris Wrote: On the picture it looks like the termination resistor on the AP scanner is swithed ON. This scanner is placed in the middle of the serial line. Because the LM port is not terminated, then both scanners in short line distances must be set in OFF position.
That makes sense, but still nothing. The DIP switch has "ON" and "1" labels. For me as a developer these both mean ON.
I have wired the two scanners in a daisy-chain topology, not star topology.
P.S. I just tried with only one scanner, both the DIP switch to ON and OFF positions. On daemon start the orange blinking LED becomes steady blue for couple of seconds and then orange blinking LED again. There's some communication, but something is wrong.