This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Problem with modbus TCP on Spacelynk 2.6.0
#4
You don't have to restart anything. By default the daemon will connect to the TCP device, read then disconnect. Persistent connection mode does not disconnect. This is needed for certain devices that have a limited number of connections available and sometimes will refuse connections.
"Invalid data" is a protocol error which means that the TCP device sent some invalid data. Can you provide remote access to this device?
Reply


Messages In This Thread
RE: Problem with modbus TCP on Spacelynk 2.6.0 - by admin - 26.04.2021, 07:38