This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

ocpp and knx homelynk
#5
(12.10.2021, 07:38)Kilogica Wrote: Hello Erwin,

I have one question: we have an EVF2S22P44R by SE, is it natively Modbus TCP compatible or not? And if not, is there some add-on to provide for making it compatible?

Thank you for your help

Yes it should have modbus as i already integrated this one on a project.. I disabled the not needed registers but kept them in the script

Code:
require('luamodbus') mb = luamodbus.tcp() -- Read Socket 1 mb:open('192.168.1.200', 502) mb:connect() mb:setslave(255) --s1AL1 = mb:readregistervalue(350, 'float32', 'w') -- Current Phase 1 --s1AL2 = mb:readregistervalue(352, 'float32', 'w') --s1AL3 = mb:readregistervalue(354, 'float32', 'w') s1ET = mb:readregistervalue(356, 'uint32', 'w') -- Energy Total --s1PT = mb:readregistervalue(358, 'float32', 'w') -- Current Power --s1VL1L2 = mb:readregistervalue(360, 'float32', 'w') -- Voltage Phase 1 - Phase 2 --s1VL2L3 = mb:readregistervalue(362, 'float32', 'w') --s1VL3L1 = mb:readregistervalue(364, 'float32', 'w') --s1VL1N = mb:readregistervalue(366, 'float32', 'w') -- Voltage Phase 1 - Neutral --s1VL2N = mb:readregistervalue(368, 'float32', 'w') --s1VL3N = mb:readregistervalue(370, 'float32', 'w') --log(s1AL1,s1AL2,s1AL3,s1ET,s1PT,s1VL1L2,s1VL2L3,s1VL3L1,s1VL1N,s1VL2N,s1VlLN) mb:close() -- Read Socket 2 mb:open('192.168.1.201', 502) mb:connect() mb:setslave(255) --s2AL1 = mb:readregistervalue(350, 'float32', 'w') --s2AL2 = mb:readregistervalue(352, 'float32', 'w') --s2AL3 = mb:readregistervalue(354, 'float32', 'w') s2ET = mb:readregistervalue(356, 'uint32', 'w') --s2PT = mb:readregistervalue(358, 'float32', 'w') --s2VL1L2 = mb:readregistervalue(360, 'float32', 'w') --s2VL2L3 = mb:readregistervalue(362, 'float32', 'w') --s2VL3L1 = mb:readregistervalue(364, 'float32', 'w') --s2VL1N = mb:readregistervalue(366, 'float32', 'w') --s2VL2N = mb:readregistervalue(368, 'float32', 'w') --s2VL3N = mb:readregistervalue(370, 'float32', 'w') --log(s2AL1,s2AL2,s2AL3,s2ET,s2PT,s2VL1L2,s2VL2L3,s2VL3L1,s2VL1N,s2VL2N,s2VL3N) mb:close() -- Sum Socket 1 and Socket 2 tET = s1ET + s2ET -- Sum energy total of socket 1 and 2 tETrounded = math.round(tET/1000,0) -- Total S + S2 from Wh to kWh s1ET = math.round(s1ET/1000,0) -- Socket 1 from Wh to kWh s2ET = math.round(s2ET/1000,0) -- Socket 2 from Wh to kWh grp.checkupdate('4/1/22', s1ET) -- Update values grp.checkupdate('4/1/23', s2ET) grp.checkupdate('4/1/19', tETrounded)
Reply


Messages In This Thread
ocpp and knx homelynk - by bvb - 11.10.2021, 19:12
RE: ocpp and knx homelynk - by bvb - 12.10.2021, 10:42
RE: ocpp and knx homelynk - by Kilogica - 12.10.2021, 07:38
RE: ocpp and knx homelynk - by Erwin van der Zwart - 13.10.2021, 18:21
RE: ocpp and knx homelynk - by Kilogica - 19.10.2021, 13:38

Forum Jump: