This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Problem Modbus profile Kostal
#14
(31.10.2021, 15:28)Hyxion14 Wrote:
(01.10.2021, 06:19)Hyxion14 Wrote: But, the reading test is for RTU, not for TCP, right?

Hi, I have updated the FW to 2021 RC2 and now I can do test for TCP from the Kostal inverter.

For example if I query register: 514 , it gives me the current battery charge value correctly.

But when I make the map, it does not give me any value.

The register I am trying to map is:

{
      "name": "Battery current SOC",
      "bus_datatatype": "uint16",
      "address": 514,
      "writable": 0,
      "unit":"%"
    }
In KNX I have created a Virtual group address at address 32/3/3 type 2 bytes unsigned integer.

Why the test works and reads the value correctly but when I do the mapping I don't get the value?

Thank you.

Problem Solved.

Attached is the json profile of the Kostal Plenticore Inverter.

I hope it will be helpful.

Attached Files
.json   Kostal_PLENTICORE_V3.json (Size: 15.75 KB / Downloads: 28)
Reply


Messages In This Thread
Problem Modbus profile Kostal - by sorrow - 14.02.2019, 10:28
RE: Problem Modbus profile Kostal - by admin - 14.02.2019, 10:37
RE: Problem Modbus profile Kostal - by sorrow - 14.02.2019, 10:50
RE: Problem Modbus profile Kostal - by admin - 14.02.2019, 11:06
RE: Problem Modbus profile Kostal - by sorrow - 25.02.2019, 12:30
RE: Problem Modbus profile Kostal - by admin - 30.09.2021, 11:50
RE: Problem Modbus profile Kostal - by Hyxion14 - 31.10.2021, 18:29
RE: Problem Modbus profile Kostal - by admin - 01.10.2021, 08:02

Forum Jump: