This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus CRC error
#4
Total length is around 25 meter, I have from LM about 10 meter 2x2x0,8 KNX BUS-cable to a junction box. From this box I have splitted the bus in 2 direction, each direction is about 7-8 meters, one goes to floor 3, and the other goes to floor 1 (LM is placed on floor 2)

Slave #1 is using 3 wires with GND (GND is connected in both LM and RTU slave)
Slave #2 is 2 wires D+ and D- only.

It is not connected as daisy-chain, because I split the Bus-cable in the junction box and send it in different directions.

I set new MB-ID to slave #1, it generated much less invalid CRC but instead more "wrong slave", see attached.
Also I have removed all mapping to Slave #2, slave to is only connected to the RS485 without having anything mapped to it, and starts making trouble for slave #1 as seen on this log.

Attached Files Thumbnail(s)
   
Reply


Messages In This Thread
Modbus CRC error - by sx3 - 31.10.2016, 20:20
RE: Modbus CRC error - by sx3 - 01.11.2016, 06:43
RE: Modbus CRC error - by admin - 01.11.2016, 07:40
RE: Modbus CRC error - by sx3 - 01.11.2016, 08:14
RE: Modbus CRC error - by sx3 - 01.11.2016, 13:27
RE: Modbus CRC error - by admin - 01.11.2016, 13:40
RE: Modbus CRC error - by sx3 - 01.11.2016, 13:52
RE: Modbus CRC error - by sx3 - 01.11.2016, 18:31
RE: Modbus CRC error - by admin - 02.11.2016, 12:24
RE: Modbus CRC error - by sx3 - 02.11.2016, 13:04
RE: Modbus CRC error - by admin - 02.11.2016, 13:09
RE: Modbus CRC error - by Angeles - 20.03.2018, 09:39
RE: Modbus CRC error - by Daniel - 20.03.2018, 12:38