Total length is around 25 meter, I have from LM about 10 meter 2x2x0,8 KNX BUS-cable to a junction box. From this box I have splitted the bus in 2 direction, each direction is about 7-8 meters, one goes to floor 3, and the other goes to floor 1 (LM is placed on floor 2)
Slave #1 is using 3 wires with GND (GND is connected in both LM and RTU slave)
Slave #2 is 2 wires D+ and D- only.
It is not connected as daisy-chain, because I split the Bus-cable in the junction box and send it in different directions.
I set new MB-ID to slave #1, it generated much less invalid CRC but instead more "wrong slave", see attached.
Also I have removed all mapping to Slave #2, slave to is only connected to the RS485 without having anything mapped to it, and starts making trouble for slave #1 as seen on this log.
Slave #1 is using 3 wires with GND (GND is connected in both LM and RTU slave)
Slave #2 is 2 wires D+ and D- only.
It is not connected as daisy-chain, because I split the Bus-cable in the junction box and send it in different directions.
I set new MB-ID to slave #1, it generated much less invalid CRC but instead more "wrong slave", see attached.
Also I have removed all mapping to Slave #2, slave to is only connected to the RS485 without having anything mapped to it, and starts making trouble for slave #1 as seen on this log.