Reading 8 coil points as a 1 byte in Modbus
It's not possible to do this via a profile, you will have to use scripts. You can access the same RS485 port from both profiles and scripts using mbproxy.
You can read multiple coils/inputs via a script and convert to a number.
function bitstonumber(bits)   local res = 0   for bnum, bval in ipairs(bits) do     if bval then       res = bit.bor(res, bit.lshift(1, bnum - 1))     end   end   return res end mb = require('mbproxy').new() mb:setslave(1) bits = { mb:readcoils(8, 8) } if #bits == 8 then   mode = bitstonumber(bits)   log(mode) else   log(bits) end
The addressing probably starts from 0 so you have to subtract 1 from the documented addresses.
Temperature will not work with "value_multiplier": 0.1, try using "datatype": "float16" and "bus_datatype": "float16" without "value_multiplier".
RE: Reading 8 coil points as a 1 byte in Modbus - by admin - 22.12.2021, 10:52