You should import the JSON profile with the variable you need.
Consider that device modbus address is number 1 (if you have only a system card) and the register variables e are calculated as follow:
register of zone = Airzone device x 256 + register address.
Example:
Set point value for the first zone is 259 instead for the second Is 515.
BR.