This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus values wrong
#11
Hello, can you help me. I have a Condair RM humidity and I want to change humidity setpoint value. Modbus address 4888 32-bit float big_endian
Example: I send 47% setpoint. I send command mb:writeregisters(4887, 47, 'B') nothing changes, but if mb:writeregisters(4887, 16956, 'B') setpoint changes to 47%.

But if I want to send 48% I don't know what value to send. How I can convert values?
Reply