Hello, can you help me. I have a Condair RM humidity and I want to change humidity setpoint value. Modbus address 4888 32-bit float big_endian
Example: I send 47% setpoint. I send command mb:writeregisters(4887, 47, 'B') nothing changes, but if mb:writeregisters(4887, 16956, 'B') setpoint changes to 47%.
But if I want to send 48% I don't know what value to send. How I can convert values?
Example: I send 47% setpoint. I send command mb:writeregisters(4887, 47, 'B') nothing changes, but if mb:writeregisters(4887, 16956, 'B') setpoint changes to 47%.
But if I want to send 48% I don't know what value to send. How I can convert values?