This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus profile generator
#25
Also writable value should be true without quotes otherwise newer firmware won't accept the profile. Addressing starts with 0 and for mode/speed registers you can use 1 byte (uint8) data type.
Code:
{   "manufacturer": "YORK",   "description": "HA-MA164AD",   "mapping": [     {       "name": "Indoor Unit Setpoint Temperature",       "address": 0,       "bus_datatype": "uint16",       "datatype": "uint16",       "type": "register",       "writable": true     },     {       "name": "Indoor Unit Mode Selection",       "address": 1,       "bus_datatype": "uint8",       "datatype": "uint16",       "type": "register",       "writable": true     },     {       "name": "Indoor Unit Fan Speed",       "address": 2,       "bus_datatype": "uint8",       "datatype": "uint16",       "type": "register",       "writable": true     },     {       "name": "Indoor Unit Control Mode",       "address": 3,       "bus_datatype": "uint8",       "datatype": "uint16",       "type": "register",       "writable": true     },     {       "name": "Indoor Unit On/Off",       "address": 0,       "bus_datatype": "bool",       "type": "coil",       "writable": true     }   ] }
Reply


Messages In This Thread
Modbus profile generator - by Daniel - 08.12.2020, 12:06
RE: Modbus profile generator - by tomnord - 08.12.2020, 15:34
RE: Modbus profile generator - by JRP - 09.12.2020, 10:17
RE: Modbus profile generator - by Trond Hoyem - 21.12.2020, 15:10
RE: Modbus profile generator - by Daniel - 21.12.2020, 15:13
RE: Modbus profile generator - by Trond Hoyem - 22.12.2020, 06:23
RE: Modbus profile generator - by JRP - 29.04.2021, 09:23
RE: Modbus profile generator - by Daniel - 29.04.2021, 09:44
RE: Modbus profile generator - by JRP - 29.04.2021, 09:52
RE: Modbus profile generator - by gdimaria - 17.11.2021, 14:30
RE: Modbus profile generator - by Daniel - 17.11.2021, 14:36
RE: Modbus profile generator - by gdimaria - 17.11.2021, 14:40
RE: Modbus profile generator - by Daniel - 17.11.2021, 14:47
RE: Modbus profile generator - by gdimaria - 17.11.2021, 14:51
RE: Modbus profile generator - by admin - 17.11.2021, 14:52
RE: Modbus profile generator - by gdimaria - 17.11.2021, 14:57
RE: Modbus profile generator - by gdimaria - 17.11.2021, 15:57
RE: Modbus profile generator - by Daniel - 18.11.2021, 10:01
RE: Modbus profile generator - by gdimaria - 18.11.2021, 16:01
RE: Modbus profile generator - by Ian@GWTi - 21.01.2022, 14:50
RE: Modbus profile generator - by Daniel - 21.01.2022, 14:52
RE: Modbus profile generator - by domotiqa - 30.03.2022, 16:37
RE: Modbus profile generator - by mkaymak - 22.06.2022, 06:40
RE: Modbus profile generator - by Daniel - 22.06.2022, 07:29
RE: Modbus profile generator - by admin - 22.06.2022, 08:07
RE: Modbus profile generator - by mkaymak - 30.06.2022, 07:51
RE: Modbus profile generator - by admin - 30.06.2022, 10:28
RE: Modbus profile generator - by mkaymak - 30.06.2022, 10:43
RE: Modbus profile generator - by admin - 30.06.2022, 10:58
RE: Modbus profile generator - by mellotron - 03.10.2023, 12:16
RE: Modbus profile generator - by Daniel - 03.10.2023, 12:21
RE: Modbus profile generator - by mellotron - 03.10.2023, 12:34
RE: Modbus profile generator - by Daniel - 03.10.2023, 14:05
RE: Modbus profile generator - by Daniel - 23.06.2025, 08:46

Forum Jump: