This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM as a Modbus slave : number of slaves
#5
If you only need read-only values on the modbus side you can simply periodically update the register values in the resident script itself. Modify register mapping in updateregisters() as needed. Each script must use a unique port (502, 503 etc).
Code:
if not mb then   require('luamodbus')   mb = luamodbus.tcp()   mb:open('0.0.0.0', 502)   mb:setslave(2)   function setint64(grpaddr, regaddr)     local value = grp.getvalue(grpaddr) or 0     local raw = knxdatatype.encode(value, dt.int64).dataraw     local r1 = raw:byte(2) * 0x100 + raw:byte(1)     local r2 = raw:byte(4) * 0x100 + raw:byte(3)     local r3 = raw:byte(6) * 0x100 + raw:byte(5)     local r4 = raw:byte(8) * 0x100 + raw:byte(7)     mb:setregisters(regaddr, r4, r3, r2, r1)   end   function updateregisters()     setint64('32/1/1', 3204)   end   mb:setmapping(0, 0, 3300, 0)   updateregisters()   prev = os.time() end mb:handleslave() curr = os.time() if curr ~= prev then   updateregisters()   prev = curr end
Reply


Messages In This Thread
RE: LM as a Modbus slave : number of slaves - by admin - 09.08.2022, 06:27