11.12.2016, 14:14
(11.12.2016, 08:39)admin Wrote: UIO20 does support 9600 and other baudrates, but once you change RTU settings through ModBus tab you have to do the write address procedure again. This will write both the new address and serial settings.
That's great news thanks, but I did not manage to change the settings, I don't have a programming button on my UIO20E device. I only see two unsoldered holes on the PCB on the bottom left, maybe I have to short these to go in programming mode ?
Can I also change parity to None using this procedure ?