13.12.2016, 09:47
(13.12.2016, 09:25)admin Wrote: PLC specifies different character encoding (ISO 8859-1) instead of ASCII/UTF8 which is used by LM. Can you check if it's a configurable property in your PLC?
That's it!
Even found a warning in the PLC's programming software - "the BACnet confirmed data communication of texts in not guaranteed!" Lost two days on this
Just checked the previous project and it is UTF-8.
Thank you for your generous help!