This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus communication lost
#8
One one of my LM I have a Modbus RS485 issue. I can get out data 1 out of 2 times. One call goes OK and I get data, second call results in a CRC error. I tried this with a readtest under Modbus. When I get a CRC error, the communication LED on the Janitza unit flashes green (that is OK).

With a profile that works on my other LM everything goes right.

I want to read out a Janitza power meter UMG20CM (it has a communication led), this device has Modbus address 1, speed 9600

I tried the following things:
a/ reverse polarity (then always crc errors, red error led on Janitza meter for communications)
b/ connect GND of LM and Janitza: no difference
c/ checked if the fase and neutral of the LM and Janiza aren't switched
d/ tried to lower speed 38400 --> 9600 
e/ tried parity al variants (now no, 1 stopbit)
f/ tried other cabling, twisted pair stranded cable

Any tips to try?
Reply


Messages In This Thread
RE: Modbus communication lost - by Daniel - 28.09.2022, 07:39
RE: Modbus communication lost - by DarthPaul - 29.09.2022, 07:38
RE: Modbus communication lost - by Daniel - 29.09.2022, 07:46
RE: Modbus communication lost - by admin - 29.09.2022, 08:03
RE: Modbus communication lost - by DarthPaul - 29.09.2022, 08:10
RE: Modbus communication lost - by admin - 29.09.2022, 08:12
RE: Modbus communication lost - by jeroen@stevens.biz - 31.10.2022, 20:28
RE: Modbus communication lost - by admin - 01.11.2022, 08:50
RE: Modbus communication lost - by admin - 21.11.2022, 08:05

Forum Jump: