This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Error on some of the addresses when reading Modbus on the Eastron SDM72DM-V2 electric
#5
Do not use read_offset, set the address directly. The real address is in the "Modbus Protocol Start Address Hex" column which is address - 30001 for input registers. Note that there's no space in "inputregister". You might need to use a different read_swap mode to get correct results. Use Read test to confirm the correct settings before making a profile.