(07.11.2022, 09:01)admin Wrote: Do not use read_offset, set the address directly. The real address is in the "Modbus Protocol Start Address Hex" column which is address - 30001 for input registers. Note that there's no space in "inputregister". You might need to use a different read_swap mode to get correct results. Use Read test to confirm the correct settings before making a profile.
Hi, Thanks for the feedback.
Yes, I noticed that read_offset doesn't help much.
I think it's auto-correction that gets the text "input registers" split up.
Is correct in the profile "inputregisters".
Regarding read_swap
Have tested all options in Read test and only None (ABCD) / "read_swap": "n" returns a correct number/answer.
I found out it is the first address I can not read.
According to the Modbus register for the electricity meter. is the first address (30001) / address 1. Phase 1 measurement. Address 30003 and 30005 have phase 2 and 3.
If I read at address 1, I get phase 2 measurement and at address 3 I get phase 3 measurement.
This also happens again at many of the other addresses, e.g. should you get the reading for Hz at address 71, but get it at 69.
If I read with another Modbus master unit, I get the correct values/responses to the addresses given in the instructions.
So it must be an LM Modbus setup I have wrong.?
Then it's just something I'm missing in my LM Modbus profile.