This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Status delay Modbus.
#3
(05.12.2022, 07:30)admin Wrote: You can set the poll interval to a lower value.
Thank you for the very quick response!
I have set the poll interval to the lowest value of 1 but the status does not update faster. If I increase baud rate to 19200 don't know the state will respond faster? The device parameter can be upgraded to 19200 baud rate but in the LM log it gives an error: (RTU 1 slave 1) read failed: Invalid CRC.