06.12.2022, 10:45
(06.12.2022, 07:42)admin Wrote: It won't be much faster at higher bitrate. Modbus is not meant for fast communication due to polling.Thanks admin!
As a work-around you can map an event script to the control object to update the status immediately.
I can write it directly in 6.1.2 as the on/off control address for state updates:
if event.getvalue()
then
grp.write('6/1/1', true) --Status on/off
else
grp.write('6/1/1', false) --Status on/off
end
Admin have any better ideas?