This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

modbus tcp error
#2
Invalid data means that the read request was not fully sent or the reply is incorrect. Most likely the profile is not at fault here, it's an issue on the inverter.

You can try enabling or disabling persistent connection mode and see if it makes a difference.
Reply