DMX-512 devices usually have either use a DIP-switch or a display to set the address. DMX-512 communication is one way so the only way to check if it's working is to see if lights can be controlled from LM.
What kind of strip are you using? Do you have GND connected between LM and the DMX controller? You can also try swapping A/B, sometimes they are labeled incorrectly.
For larger installations it is recommended to use an external Ethernet-DMX gateway that uses ArtNET protocol. See examples here: https://forum.logicmachine.net/showthread.php?tid=1391