This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus poll issue
#2
Profile looks correct. Several things to try:
1. Enable persistent connection mode for each device.
2. Connect GND between gateway and all other Modbus devices on the same line.
3. Add read_delay to the profile. Start with a small value like 0.1 or 0.2 seconds.
Reply