This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

M-bus problem
#7
Try setting a lower baudrate (2400) on both LM and the meter. It's possible that RS485 is damaged on the meter if you've connected M-Bus there - not all RS485 ports are protected against 24V DC connection. There's also a similar meter model with Modbus instead of M-Bus.
Reply