But instead of sending notifications you should find the root cause and fix it. This is usually caused by having too many KNX devices on a single KNX/TP line and sending too many telegrams to the TP bus from LM. Things to consider:
- Check that scripts use grp.checkwrite instead of grp.write where appropriate.
- Check that Modbus send delta and write to bus is setup according to the project needs.
- Install Group monitor app on LM and check if there are any duplicate telegrams.