25.05.2023, 16:28
(This post was last modified: 25.05.2023, 18:17 by CristianAgata.)
(25.05.2023, 11:41)admin Wrote: Status monitoring script: https://forum.logicmachine.net/showthrea...66#pid3466
Temperature warning code is 0x0F
But instead of sending notifications you should find the root cause and fix it. This is usually caused by having too many KNX devices on a single KNX/TP line and sending too many telegrams to the TP bus from LM. Things to consider:
- Check that scripts use grp.checkwrite instead of grp.write where appropriate.
- Check that Modbus send delta and write to bus is setup according to the project needs.
- Install Group monitor app on LM and check if there are any duplicate telegrams.
Thanks for the help.
Yes, I'm agree with you, my will it is to know when there is the problem. Because in this way I hope to catch the right moment and understand who generate the problem.
Best regards Cristian