This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

"Connect" modbus devices
#7
Based on the standard yes you should not write to inputregisters but manufactures not always fallow the standard Smile
I don't know DE but seems the description below the table says it is float32.
Try different settings and if nothing helps contact manufacture to clearly describe which modbus function you should use for reading and writing and the format.
------------------------------