(01.02.2024, 12:25)admin Wrote: LMs automatically exchange object values via KNX/IP. Looping is caused when both LMs are connected to the same TP line, so don't connect the second LM to KNX/TP. Set KNX connection mode to IP routing on it. Then adjust KNX filters on both LMs to only send what's needed.