If you have the values in the AS-P and btw thats not a PLC (: why don’t you just create objects in the LM and expose them to BACnet, do a discovery in the AS-P and bind your objects in the AS-P to the discovered objects?
Another way is creating a Modbus slave network in the AS-P and expose the needed modbus objects to TCP so the LM can read them.
I would definitely go for option 1, few minutes work…
PS: Why are all meters offline in the AS-P? Did you set the correct polling register for online status?