This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

SpaceLynk Schneider & PASS600
#4
Then you need to create a Modbus profile for the SpaceLYnk where the registers for digital input is present. See here for documentation:

Documentation

As you can see, depending on the way you set up the digital input, you need to specify the correct register. Remember to subtract 1 from the register in the document for the SL to get data from it.

You add the PAS with its IP as a Modbus TCP/IP device in SL, with address 255. Use your created and uploaded profile.
Reply