Hi,
just to check - by default your EL Modbus Meter ID (Slave adress) =1? (You put =1) This is very important. It depends from device. For some others it could be 254 by default.
If you have many of meters or other devices connected to line - individual adress should be set for every device and also the same communication parameters for all line devices.. If you will have 2 or more the same adreses - communication will not work.
Any other devices are connected??
Alexander