Multi-proxy modbus connection
Hi everybody!
I have a problem about modbus writing.
In this work there is two airconditioning connected to modbus and it have the same modbus ID (49). I can't change it because the company don't allow it.
I connected this two device to the two different port of RS485.
But the problem is to open comunication with proxy. You can't specificate where it have to open comunication.
I use this script:
-- get value of object with group address 1/1/1 setpoint_z2 = grp.getvalue('1/1/1') setpoint_z2_mb = setpoint_z2*2 -- proxy works only when RTU is enabled in Modbus settings mb = require('mbproxy').new() mb:setslave(49) -- set register at address 6 mb:writeregisters(6, setpoint_z2_mb) -- read from address 6 value_rmb = mb:readregisters(6)
Multi-proxy modbus connection - by gianluca_depascali@hotmail.it - 09.09.2024, 09:00
RE: Multi-proxy modbus connection - by admin - 09.09.2024, 09:21