This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus problem
#2
Go to Modbus tab and enable the required RTU port. Make sure that your Modbus devices have the same baud, parity and stop bit settings. Then use Read test to check the communication.
It's highly recommended to connect GND/0V between LM and Modbus device. In some rare cases RS-485 A/B is marked incorrectly and should be swapped.
Reply


Messages In This Thread
Modbus problem - by BMSimon - 04.10.2024, 07:19
RE: Modbus problem - by admin - 04.10.2024, 08:00
RE: Modbus problem - by BMSimon - 04.10.2024, 08:36
RE: Modbus problem - by admin - 04.10.2024, 08:40

Forum Jump: