This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM bus connection fault
#5
(8 hours ago)Daniel Wrote: Drop screenshot of KNX settings and KNX statistics

Hi Daniel,
I unplug step by step some group of devices to verify if problem can be related to some devices in fault. 
In ETS bus monitor nothing strange (max load bus Is 20%) when Siemens Sincos (8 devices) send on bus telegrams   of temperature, status of valves and so on. Consider that facility has only 10 devices connected.

Bus voltage Is 29 volts and there Is no overload on Power supply. But in some case telegrams are not sent. Neither from LM neither from devices on bus. 

Is there a way from LM to monitor the bus voltage? 

Thanks.