This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

UTA UTEK MODBUS
#10
You need to set the timeout value to max (65535) to disable it. As stated in the documentation:
TEMPO DI SCONNESSIONE
DEFAULT=10 SEC.
65535 DISABILITA LA SCONNESSIONE IN CASO DI MANCATA LETTURA DEI REGISTRI

Alternatively you can set poll interval to be lower than the timeout. But then the value reset will still happen if LM is rebooted and the timeout is reached.